Default How to bypass an oil sensor to test

I have a 7000kw unit, no sense in telling you the model number as no one can find it, not even generac (it is gasoline/propane). Typical house unit, not portable.

It runs for a minute then shuts off. How do I test the cutoff sensors, like oil sensor? Do I jump the two wires going into it?

What other sensors do I look for?

Thanks!
ricor is offline   Reply With Quote
Old October 18th, 2010   #2
Dennis
Junior Member
 
Join Date: Sep 2010
Posts: 12
Default

I think you just need to remove one of the wires off the sensor. When the wires are connected, the enging will shut down. The only other sensor you might have is an over temp and that would be tested the same way. Good luck

ps: I found a manual for a 9067-0. The quality is poor but it is better than nothing. I have the -8 model that has a larger engine than the one listed for the -0. I also found a manual for a 10k that looks a lot like the 8k. If you want I will look for the info and post it here.

Last edited by Dennis; October 18th, 2010 at 08:17 PM..
Dennis is offline   Reply With Quote
Old October 18th, 2010   #3
SkipD
Moderator
 
SkipD's Avatar
 
Join Date: May 2008
Location: Southeastern Wisconsin
Posts: 2,925
Default

"Fail-safe" sensors which are essentially switches would normally be "made" when the applied variable is "normal".

In other words, a low oil pressure sensor is probably a switch which is "made" when the pressure is normal for running an engine.

Opening the wires by pulling a connector off the sensor (which is a switch) would probably emulate an alarm condition. If this is true, then shorting the wires (or shorting a single wire connection to ground) would emulate a "normal" condition.

Before I would defeat a low oil pressure sensor, for example, I would MEASURE the variable and determine if the condition is in fact safe for the engine. For this example, I would remove the pressure sensor from the engine and install a reliable pressure gauge. Then, attempt to start the engine. Since pressure will not build up in the sensor, the engine won't continue to run. However, you should see the oil pressure build up to normal on the gauge if the only problem is a bad sensor.

I can go on and on if you need more.
__________________
Skip Douglas
SkipD is offline   Reply With Quote
Old October 18th, 2010   #4
Dennis
Junior Member
 
Join Date: Sep 2010
Posts: 12
Default

The one that is close is an 8k not 10k. It is an 0865-0. This has a 570cc engine that my -8 model has. I will look for the download link for the -0 model that has a 480cc engine.

Here is the download link for the 9067-0
http://www.hammerwall.com/Download_Manual/4262/

After it opens you can save it to your hard drive. Again the quality is poor and the engine size may be different but the info should help.

Last edited by Dennis; October 18th, 2010 at 08:22 PM..
Dennis is offline   Reply With Quote
Old October 18th, 2010   #5
Gman1
Senior Member
 
Join Date: Nov 2007
Posts: 144
Default

In the older units, you could just unplug/remove the wire from the op switch. If it runs, you either have a bad switch...or no oil pressure. On the newer units the switch has to be closed for the engine to crank and then open before the board "looks" for oil pressure. In the latter case, ground the sensor wire, crank the unit, and then immediately un-ground the wire. Hope this helps.
Gman1 is offline   Reply With Quote
Old October 18th, 2010   #6
SkipD
Moderator
 
SkipD's Avatar
 
Join Date: May 2008
Location: Southeastern Wisconsin
Posts: 2,925
Default

Quote:
Originally Posted by Gman1 View Post
In the older units, you could just unplug/remove the wire from the op switch. If it runs, you either have a bad switch...or no oil pressure. On the newer units the switch has to be closed for the engine to crank and then open before the board "looks" for oil pressure. In the latter case, ground the sensor wire, crank the unit, and then immediately un-ground the wire. Hope this helps.
I verified this in the diagnostic manual for my 5416. What I said above about "fail-safe" sensors is true, but it's apparent that the sensors - at least the oil pressure sensors - in Generac generators are NOT fail-safe.

A fail-safe system is designed to trip if a wire is inadvertently cut or a connector falls off in the sensing circuit.

In my generator, at least, the oil pressure sensor opens a contact as acceptable oil pressure is reached.

To test the safety circuit, I would put a gauge in place of the sensor and short the lead that went to the sensor to ground. Then, test start the generator while watching the pressure gauge. If pressure starts to rise in a way that seems normal, remove the sensor lead from the grounding connection and the engine should continue to run. Shorting the sensor lead back to ground should cause the engine to fault and shut down.
__________________
Skip Douglas
SkipD is offline   Reply With Quote
Old October 19th, 2010   #7
techntrek
Senior Member
 
Join Date: Feb 2010
Location: MD north of Baltimore
Posts: 699
Default

Actually the newer system sounds better. It tests that the switch changes state (on/off) from before starting to after starting.
techntrek is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 12:41 AM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Copyright 1985-2016 Ziller Electric Inc
Ziller Electric Inc is not representing Generac Power Systems Inc