Default LP vapor or liquid supply?

Do home generators, e.g., Generac, draw LP vapor from the tank or do they draw liquid and use a vaporizer at the engine to cause the LP to change phase for use by the engine?
rico567 is offline   Reply With Quote
Old September 14th, 2011   #2
Ira
Senior Member
 
Join Date: Jun 2008
Posts: 188
Default

In my case, it's a "standard" LPG setup, so it draws vapor. The gas appliances in my home are supplied by the same line from the tank as my genset.
Ira is offline   Reply With Quote
Old September 14th, 2011   #3
SkipD
Moderator
 
SkipD's Avatar
 
Join Date: May 2008
Location: Southeastern Wisconsin
Posts: 2,888
Default

I've never heard of any home generator using LP in liquid form. All of them that I've heard about use vapor from the tank like any other conventional LP appliance.
__________________
Skip Douglas
SkipD is offline   Reply With Quote
Old September 14th, 2011   #4
rico567
Senior Member
 
Join Date: May 2011
Location: E Central IL
Posts: 118
Default

I encountered a reference by someone who claimed that home generators used liquid LP, but it didn't make sense, particularly with an air-cooled generator. The vaporizers operate by using engine coolant. I believe the person making this assertion had conflated home generators with large equipment using LP. So- I think this question has been resolved to my satisfaction.
rico567 is offline   Reply With Quote
Old September 14th, 2011   #5
dsc3507
Junior Member
 
Join Date: Sep 2011
Posts: 25
Default

Maybe the misunderstanding was because the Generac's are advertised as (spelled out) Liquid petroleum or Natural gas in the description. How would a device that actually ran on the liquid form receive it? I suspect it would need to be pumped or gravity fed like any other liquid fuel.
dsc3507 is offline   Reply With Quote
Old September 14th, 2011   #6
SkipD
Moderator
 
SkipD's Avatar
 
Join Date: May 2008
Location: Southeastern Wisconsin
Posts: 2,888
Default

Quote:
Originally Posted by dsc3507 View Post
I suspect it would need to be pumped or gravity fed like any other liquid fuel.
LP in a tank is under fairly high pressure (which varies significantly with the temperature), and this is quite unlike any other "normal" liquid fuel that I'm aware of.
__________________
Skip Douglas
SkipD is offline   Reply With Quote
Old September 14th, 2011   #7
rico567
Senior Member
 
Join Date: May 2011
Location: E Central IL
Posts: 118
Default

Quote:
Originally Posted by SkipD View Post
LP in a tank is under fairly high pressure (which varies significantly with the temperature), and this is quite unlike any other "normal" liquid fuel that I'm aware of.
Quote:
Originally Posted by dsc3507 View Post
Maybe the misunderstanding was because the Generac's are advertised as (spelled out) Liquid petroleum or Natural gas in the description. How would a device that actually ran on the liquid form receive it? I suspect it would need to be pumped or gravity fed like any other liquid fuel.
I don't know about the pump, but when I went to several sites reading up on this, evidently there's a device called a "vaporizer" (the closest analog would be a carburetor in a gasoline engine) that converts the liquid fuel to vapor, using the heat of the engine's coolant to accomplish this. It seems to be for large engines in mobile equipment, where having a large tank to accomplish the vaporization in the empty space above the fuel would be impractical.
rico567 is offline   Reply With Quote
Old September 14th, 2011   #8
Jack Hottel
Member
 
Join Date: Jun 2009
Location: Haymarket, VA
Posts: 33
Default

LP liquid withdrawal just requires a tank outlet with a dip tube to near the bottom. At any temperature above -40 the vapor pressure in the tank will force the liquid out. At the point of use the liquid must be vaporized in a heated vaporizer, which often also contains the necessary regulators. These vaporizers are often heated by the coolant of liquid cooled engines, but vaporizers do exist which are designed to be heated by the cooling air from an air cooled engine. Small engines are usually vapor fed, but liquid can be and is used. Larger engines are usually liquid fed.
Jack Hottel
Jack Hottel is offline   Reply With Quote
Old September 15th, 2011   #9
ike
Junior Member
 
Join Date: Aug 2011
Location: west of the windy city
Posts: 12
Default

Quote:
Originally Posted by Jack Hottel View Post
LP liquid withdrawal just requires a tank outlet with a dip tube to near the bottom. At any temperature above -40 the vapor pressure in the tank will force the liquid out. At the point of use the liquid must be vaporized in a heated vaporizer, which often also contains the necessary regulators. These vaporizers are often heated by the coolant of liquid cooled engines, but vaporizers do exist which are designed to be heated by the cooling air from an air cooled engine. Small engines are usually vapor fed, but liquid can be and is used. Larger engines are usually liquid fed.
Jack Hottel
I have read that some older generators exhaust were pointed on the propane tanks or lines to heat them ( vaporize) as well. Interesting reading for sure!
ike is offline   Reply With Quote
Old September 15th, 2011   #10
douglas123
Senior Member
 
Join Date: May 2011
Location: memphis,tn.
Posts: 476
Smile

That would be true. In colder climates folks installed their propane tanks in front of the radiator end of liquid cooled engines to allow the warmer air to blow on the tank to raise the temperature Liquid propane is a marvel in itself. Would love to discuss further, just don't have the time right now.
douglas123 is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 01:48 AM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Copyright 1985-2016 Ziller Electric Inc
Ziller Electric Inc is not representing Generac Power Systems Inc