Ziller Electric Inc | Interactive Generac Generator Forum  

Go Back   Ziller Electric Inc | Interactive Generac Generator Forum > Generac Generator Tech Talk > Generac Automatic Transfer Switches

ZillerElectric.com Generac Guardian 22kW 7043 Generator Generac iQ2000 2000 Watt Inverter Generator

Generac Automatic Transfer Switches Troubleshooting Information About Air Cooled Generac Generators. Feel free to ask questions!

Reply
 
Thread Tools Display Modes
Old January 19th, 2012   #1
Richard
Member
 
Join Date: Dec 2011
Location: Southeast, Louisiana
Posts: 35
Default Surge protection for an ATS

Is the purchase of a surge protector placed between the utility in put and the ats cost effective. How would I know if the surge suppressor did any good and actually protected the ats? Please can someone please help me make the right selection or decision?

Thanks
Richard is offline   Reply With Quote
Old January 19th, 2012   #2
SkipD
Moderator
 
SkipD's Avatar
 
Join Date: May 2008
Location: Southeastern Wisconsin
Posts: 2,859
Default

There's really nothing that a surge protector on the utility power feed can do to protect an ATS.

I'm assuming a whole-house generator system in saying this: If you were going to install a large surge protector, it should be located between the ATS and the distribution (breaker) panel so that it works for both utility and generator power.
__________________
Skip Douglas
SkipD is offline   Reply With Quote
Old January 20th, 2012   #3
ceb58
Senior Member
 
Join Date: Nov 2009
Location: NC
Posts: 1,215
Default

Quote:
Originally Posted by SkipD View Post
There's really nothing that a surge protector on the utility power feed can do to protect an ATS.

I'm assuming a whole-house generator system in saying this: If you were going to install a large surge protector, it should be located between the ATS and the distribution (breaker) panel so that it works for both utility and generator power.
And to add to that, you would need surge protection between the utility and ATS and between the gen. and ATS for protection of the ATS. But for a little peace of mind a lot of power companies offer whole house suppressors that plug into the meter base. The bottom line is you are more at risk from a surge on the utility side than the generator side.
__________________
Sure it will work.... I saw it on YouTube
ceb58 is offline   Reply With Quote
Old January 21st, 2012   #4
genme
Senior Member
 
Join Date: Apr 2011
Location: SW VA
Posts: 691
Default

Do the three 5 amp fuses in a service rated transfer switch provide any surge protection (N1, N2, T1)?
__________________
5875 20kW Nexus air-cooled, LP
RTSD200A3 service rated T.S.
new 2011 install w/cold weather kit
0058750, 6199xxx
genme is offline   Reply With Quote
Old January 21st, 2012   #5
d11gnccer
Senior Member

 
Join Date: Jul 2008
Location: Columbus, Ohio
Posts: 696
Default

Quote:
Originally Posted by genme View Post
Do the three 5 amp fuses in a service rated transfer switch provide any surge protection (N1, N2, T1)?
No. They are only in place for the sensing and battery charger circuits to protect from over current... such as a short to ground from a skinned wire.
d11gnccer is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 12:20 PM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Copyright 1985-2016 Ziller Electric Inc
Ziller Electric Inc is not representing Generac Power Systems Inc