Ziller Electric Inc | Interactive Generac Generator Forum  

Go Back   Ziller Electric Inc | Interactive Generac Generator Forum > Generac Generator Tech Talk > Generac Air Cooled Generators

ZillerElectric.com Generac Guardian 22kW 7043 Generator Free Generac Pressure Washer Banner

Generac Air Cooled Generators Troubleshooting Questions, Answers, and Information About Air Cooled Guardian Generators

Reply
 
Thread Tools Display Modes
Old March 28th, 2007   #1
Pakal
Junior Member
 
Join Date: Mar 2007
Posts: 21
Default Propane tank

Hi there, I do not have natural gas supply where I live , I could only connect a 100 lb Propane gas round tank to the generator. What gas regulator do I need to use between the tank and the generator ?
Pakal
Pakal is offline   Reply With Quote
Old June 23rd, 2007   #2
Pakal
Junior Member
 
Join Date: Mar 2007
Posts: 21
Default Propane tank

Hi again Kelly, I never got an answer to my question. Would a simple regulator, like the one I use to supply my stove, be OK for the generator. Furthermore the GPL tank will only supply the generator . How long would it last (100 lb) if connected to a 7kw or a 10kw guardian ?
Thanks for your time,

Pasquale
Pakal is offline   Reply With Quote
Old June 23rd, 2007   #3
Geoff Z
Forum Administrator

 
Geoff Z's Avatar
 
Join Date: Jan 2007
Posts: 1,182
Default

Hi Pakal, sorry for overlooking your question!

1st off, I'm NO fuel expert, I'm just an electrician. What we have experienced with 100 lb tanks, is they freeze up! I'm sitting on my deck, so I don't have my stat sheets, but the 7/10kw should be around a gallon/hour @ 50% load. I will correct this number on monday. I'm not sure how a pound resolves to gallons. I really wish someone who knows fuel could start posting here! I might have to find somebody to help out!

I'm not sure if the normal household regulator will work, because I believe you normally need two. One to drop pressure, and one to adjust W.C.
Geoff Z is offline   Reply With Quote
Old June 23rd, 2007   #4
cosmicvoid
Senior Member
 
Join Date: Apr 2007
Location: Western WA, USA
Posts: 112
Default

I'm not a fuel expert, either, but recently I did a lot of research on regulators and gas flow. You do need two stages of regulation for LPG. The first stage (red housing) drops the tank pressure (25~200 psi) down to 10 psi, the second stage (green housing) drops the 10 psi down to 11"wc. It is common to see integral 2 stage regulators that combine both into one gray housing.

Here is a pdf catalog from a valve company, but in the middle section, about pages 71~87, there is a large amount of really useful info about how the valves/regulators work, and tables for gas flow, pipe sizing, etc. It will probably answer many of your questions. There is a 'rule of thumb' chart for gas flow vs temperature and tank shape (surface area of liquid propane), and a lot of discussion about 100 lb DOT cylinders, and freeze-up.

http://www.sherwoodvalve.com/pdf/lpg.pdf

Hope this helps.

Last edited by cosmicvoid; June 23rd, 2007 at 10:25 PM..
cosmicvoid is offline   Reply With Quote
Old June 26th, 2007   #5
irq3
Junior Member
 
Join Date: Jun 2007
Posts: 23
Default

Take a look at this webpage:
http://www.propane-generators.com/lp_gas.htm

(Rules of thumb)
*It requires 2 horsepower to produce 1000 watts of energy per hour

*Under load, each horsepower consumes 10,000 BTU per hour

*LP Gas contains 92,000 BTU per gallon

The regulator size you need depends on the size of the generator (they are rated in BTU's/ HR).

For example: a 4,000 watt generator = 8 HP engine X 10,000 BTU/HR = 80,000 BTU/HR (full load). The example would need a regulator capable of handling 80,000 BTU/ HR capacity.

Pay special attention the "Vaporization Rates of Cylinders" (at 25% full) chart too. Depending on the size of the generator, if you live in a colder climate, the 100# cylinder may be too small (and freeze up).

As for needing a two stage regulator, it also depends on the BTU/HR load, distance to the propane tank, and the size of the gas line. You may be able to use a single stage regulator (11-14" WC).

This site also has a hook up hose sizing chart:
http://www.propane-generators.com/hook-up_hoses.htm

Remember, the NFPA gas code requires a propane tank to be at least 10 feet away from a combustible source (generator, etc.). Also, use a rubber flexible hose to connect the generator (vibration)!

Your best bet may be to lease a 420# tank and regulator from a gas company, have them install and fill it as needed. Usually, you get a better price on propane when buying in bulk or pre-buy.
irq3 is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 12:43 AM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Copyright 1985-2016 Ziller Electric Inc
Ziller Electric Inc is not representing Generac Power Systems Inc